I would like to build a larger shop but first need to get the land cleared and leveled. I would like to run 115/230 to the shop. The nearest power pole and meter base is about 240 feet away. Is that too far to run an underground electrical wire or will I need to set another power pole and meter base? I was hoping I could run the wire underground without having to buy another pole and meter base. By the way, I will hire a licensed electrician to do this work as I know nothing about electrical wiring. I was just trying to determine my options. Thanks for your time.
As far as voltage drop .....things to remember.....
you MUST count BOTH ways......
so you have a 480 feet plus anything else - call it 500 feet.
for example - 10 gauge wire has a bout 1 ohm per 1000 feet.....bigger wire, less resistance and will hold more amps at rated voltage.
BUT more importantly is the voltage drop is determined by max amp load.
SO based on a 240 foot run - you will need 1 gauge copper to handle 40 amps at a 2.5% drop. SO copper is not something you are going to buy ....so at the very minimum - you will need 2 ought alum. 40 amps may not be enough for you .....I would go big - just in case!!!
I would put in a 100 amp sub box and run service cable (alum)to it!