Weak air conditioning

lawnmower

New member

Equipment
L4330
Sep 9, 2025
6
0
1
tennessee
I have a 2009 L4330 with 750 hr. When engine rpm is below 1800 the air does not cool. I have cleaned condinser and evaprator, put in a heater line shut off, the belt is tight and there is no evidence of the cluch sliping. When engine is above 2200 rpm low side is around 45psi and high side is around 120 to130 psi it cools to about 12 to 14 degrees below ambiant, but below 1800 rpm there is no cooling. I don`t believe the system has ever ben opened so air and mosture are unlikley. I have had the tractor for 7 years, before that it had only had dealer service. Does anyone have an idea what could be wrong or a way to improve Airconditioning??
 

chim

Well-known member

Equipment
L4240HSTC with FEL, Ford 1210
Jan 19, 2013
2,686
2,004
113
Near Lancaster, PA, USA
Meaningful pressure readings require knowing the ambient temperature. Your high side pressure reading could be OK or 100# too low. I'm guessing it's low. Here's a pic of a thermometer stuck into a vent on my L4240 on a hot day.
 

Attachments

lawnmower

New member

Equipment
L4330
Sep 9, 2025
6
0
1
tennessee
Ambiant temp was 80 deg. F with a low side psi of 45 and high side of130 psi. at 2200 rpm. If i drop the rpm to 1000 the low side goes to 60 and high side drops to 110 psi.
 

Old Machinist

Well-known member

Equipment
Kubota LX3310 cab, JD 4310, NH 575E cab backhoe, JD F725, Swisher 60", etc.
May 27, 2024
442
482
63
NE FL
I would evacuate, vacuum, and recharge with the correct amount of refrigerant to start.
 
  • Like
  • Love
Reactions: 1 users

Fedup

Active member
Apr 6, 2016
326
126
43
Winchester
In my experience your pressures are way off. I've rarely seen a system (R134A) run properly at over 25 PSI on the low side. I usually get get good results between 15 and 20 on a hot day. Your high side seems way low to me. I'd expect 150 to maybe near 300 on a hot day, particularly so on Kubota systems with a small condenser and usually so far in front of the radiator. At lower RPM there is little or air flow through it so pressures usually get pretty high. If you see 130 PSI and it's working at all that sounds strange to me.

As for being low on charge. Possible, yes. What is the static charge with system off and pressures equalized? On an 80 degree day I would expect to see 70 to 75 PSI on both sides.
 
  • Like
Reactions: 1 users

lawnmower

New member

Equipment
L4330
Sep 9, 2025
6
0
1
tennessee
I went to the garage and checked, the temp is 75 today and engine off psi was 80psi on high side and a little over 75 on low side. I started the engine with the air on high and the high side went to about 95psi and the low went to about 65 psi with the engine at 1000 rpm. I am not fimilar with 134A systems, I worked on auto air conditioning back in the R-12 days. I defenatly don`t have even close to the pressures you listed. Were to look first is the big question?
 

DaveFromMi

Well-known member

Equipment
L3901 RCR1260
Apr 14, 2021
643
642
93
Indiana
Ok, recharge first. If that doesn't change things, could be a faulty TXV or compressor.
 
  • Like
Reactions: 1 user

lawnmower

New member

Equipment
L4330
Sep 9, 2025
6
0
1
tennessee
I will recharge, but if i`m going to empty the system vacccum it and charge it I can change the expansion valve and dryer for about $70 or $80 bucks more with after market parts. This would give me more info as to the condition of the compressor. I think that is the direction I will take. Has anyone had good experiance with after market air parts? I see ads for a hole new after market air system for my tractor for under a $1000 bucks. Has any one tried the after market parts?
 

Fedup

Active member
Apr 6, 2016
326
126
43
Winchester
Your static pressure is about right, certainly not low. The pressure differential in the system is the primary job of the expansion valve. The pressures you're seeing now tell me your valve isn't closing down quite enough while in operation. Low side pressure is too high, the high side pressure is too low. I'm surprised you get much cold air at all. If this were my project I would be replacing the valve and the drier and see what effect that has. I would get Kubota parts, not after market. Your choice.
 

Old Machinist

Well-known member

Equipment
Kubota LX3310 cab, JD 4310, NH 575E cab backhoe, JD F725, Swisher 60", etc.
May 27, 2024
442
482
63
NE FL
What should my pressures be on a 80deg day at 1000 rpm?
Ideally not more than 30 psi on the low side or 250 PSI on the high. Results can vary depending on humidity and other conditions.

When the compressor clutch turns off the pressures will begin to equalize.
 
  • Love
Reactions: 1 user

Old Machinist

Well-known member

Equipment
Kubota LX3310 cab, JD 4310, NH 575E cab backhoe, JD F725, Swisher 60", etc.
May 27, 2024
442
482
63
NE FL
I will recharge, but if i`m going to empty the system vacccum it and charge it I can change the expansion valve and dryer for about $70 or $80 bucks more with after market parts. This would give me more info as to the condition of the compressor. I think that is the direction I will take. Has anyone had good experiance with after market air parts? I see ads for a hole new after market air system for my tractor for under a $1000 bucks. Has any one tried the after market parts?
Not used any parts on my Kubota AC but I have used aftermarket parts on my cars and backhoe without any problems.
 

jaxs

Well-known member

Equipment
B1750HST
Jun 22, 2023
952
730
93
Texas
I will only add one thing, do what you please with the information. ANY SYSTEM with 134a in it (full charged, half charged or overcharged ) will have static pressure 78.6 +/- at 75f ambient.
 

psdstu

Member

Equipment
M7060HDC, L4060 HTSC, B2601, RTV1140
Dec 20, 2015
38
11
8
Marianna
In my experience your pressures are way off. I've rarely seen a system (R134A) run properly at over 25 PSI on the low side. I usually get get good results between 15 and 20 on a hot day. Your high side seems way low to me. I'd expect 150 to maybe near 300 on a hot day, particularly so on Kubota systems with a small condenser and usually so far in front of the radiator. At lower RPM there is little or air flow through it so pressures usually get pretty high. If you see 130 PSI and it's working at all that sounds strange to me.

As for being low on charge. Possible, yes. What is the static charge with system off and pressures equalized? On an 80 degree day I would expect to see 70 to 75 PSI on both sides.
Curious about the 15 to 20 low side pressure. Most of the Kubota Tractors run between 20 - 28 on the Low side with the Low Pressure switch set at 28 psi.
How does the system operate at that low range when the LP switch kicks off the compressor at 28 psi, never allowing the system to drop to 20-28 psi?
 

Tx Jim

Well-known member
Lifetime Member

Equipment
M7040 HDC & JD 4255
Apr 30, 2013
1,251
159
63
Coyote Flats,Texas
If that tractor was under my supervision & it had a very clean exterior of radiator, condenser, evaporator & cab filters I'd add more refrigerant to get pressure up to match chart shown below for your current ambient temperature. With 80°F ambient temp your tractors AC system high pressure should be 175-210 psi not 130 psi.
 

Attachments

lawnmower

New member

Equipment
L4330
Sep 9, 2025
6
0
1
tennessee
It will take me a couple weeks to get the parts and do the work but at least I have a plan of action now. Thanks for sharing your know how. I will post when work is finished.
 

Fedup

Active member
Apr 6, 2016
326
126
43
Winchester
Curious about the 15 to 20 low side pressure. Most of the Kubota Tractors run between 20 - 28 on the Low side with the Low Pressure switch set at 28 psi.
How does the system operate at that low range when the LP switch kicks off the compressor at 28 psi, never allowing the system to drop to 20-28 psi?
The low pressure switch is on the high side. That side should never be below 30 or so PSI. If static pressure is at 30 or less the system should not be operating.
 
  • Like
Reactions: 1 users

Spam Bot

Member

Equipment
Windows Computer
Aug 3, 2024
75
43
18
Austin, Minnesota
Try adding a 12 oz can of R134A to the system (without the "sealer" ) and see if it makes a difference. If it does, then you can decide if you want to add more or just evacuate and refill. To do the job correctly, you need to know how much is in the system, just like you did with the R12 and only fill to the specification. Sometimes you don't have the luxury of doing it this way, so adding some slowly might be the best that you can do. On the R12 systems, you had the sight glass to assist in getting the charge close.