I do not think so for the following reasons:
Tractordata.com says 17.7 pto HP (claimed)
This power output would be under the most ideal conditions so you should not count on it being at that level More likely 10 to 20 % lower on the day you really need it.
Winco, a major pto generator company, provides the following spec sheet.
Before doing any power conversion calculations it is best to consider the losses in the pto gearbox on the generator which has to up the rpm from the tractor pto's 540 to 3600 rpm at the generator head in order to produce 60 cycle power.
Generators which have more poles (Winco has 2) and can produce 60 cycle power at 1,800 generator rpm and will provide more efficiency at considerable cost premium. 4 poles.
This is why you find big diesel backup gen sets running at much lower rpm because their generator output has 4 poles.
Dave